Before sizing a single breaker or cable, every electrical engineer must answer one question: how much current will this motor actually draw?
THREE-PHASE MOTOR CURRENT FORMULA:
I (A) = (P × 1000) / (√3 × V × η × PF)
Where:
P = motor rated power (kW)
V = supply voltage (line-to-line)
η = motor efficiency
PF = power factor
√3 (1.732) = three-phase constant
WORKED EXAMPLE: P = 15 kW | V = 400V | η = 90% | PF = 0.85
I = (15 × 1000) / (1.732 × 400 × 0.9 × 0.85)
I = 15,000 / 529.6
I = 28.3 A
This current value determines everything downstream: circuit breaker rating, cable size, contactor rating, and overload relay setting. Get it wrong and you either trip constantly (undersized protection) or fail to protect the motor at all (oversized protection).
This exact calculation is performed on every industrial motor installation worldwide before a single wire is connected.
Save this — essential reference for any electrical or industrial automation engineer.
#MotorCurrent #ElectricalEngineering #ThreePhasePower #IndustrialAutomation #EngineeringFormulas #STEM
(번역)
하나의 차단기나 케이블 크기를 크기 전에 모든 전기 엔지니어는 한 가지 질문에 답해야 한다:
이 모터는 실제로 얼마나 전류를 그릴 것인가?
3상 모터 전류 공식:
I (A) = (P × 1000) / (√3 × V × 3 × PF)
어디:
P = 모터 등급 파워 (kW)
V = 공급 전압 (선 대 선)
η = 운동 효율성
PF = 파워 팩터
√3 (1.732) = 3 단계 상수
작업된 예: P = 15 kW | V = 400V | η = 90% | PF = 0.85
I = (15 × 1000) / (1.732 × 400 × 0.9 × 0.85)
I = 15,000 / 529.6
I = 28.3 A
이 현재 값은 모든 다운스트림을 결정합니다: 회로 차단기 등급, 케이블 크기, 컨택터 등급, 과부하 릴레이 설정. 잘못 알고 계속 (저대형 보호) 이동하거나 모터를 전혀 보호하지 못하거나 (과대형 보호).
이 정확한 계산은 전 세계 모든 산업용 모터 설치에서 수행됩니다.
저장하세요 - 모든 전기 또는 산업용 자동화 엔지니어에 대한 필수적인 참고.
#MotorCurrent #ElectricalEngineering #ThreePhasePower #IndustrialAutomation #EngineeringFormulas #STEM
전기 제어 종류