Type of Lifts Passenger Lifts – Traditional traction utilising the machine room above.
No. of Lifts Two (Duplex)
Contract Load 21 person, 1600 Kgs
Additional Load for
Stone Car Flooring 200Kgs
Contract Speed 1.6 metres/second
Levels Served Six, (Lower Ground, First, Second, Third, Fourth and Fifth)
Stops/Openings 6/6 Entrances at front only
Travel Height 20.25 metres To Be Confirmed by CONTRACTOR
Supply 400 Volts + 10% - 6% /3/50/4
Internal Car Size 1950mm wide x 1750mm deep x 2200mm high
Drive System Traction Machine
Motor Control Closed loop V.V.V.F
Levelling Accuracy + 6mm
Starts Per Hour 120 starts per hour
Control System Duplex fully collective push button control.
This system must have the built in facility to operate as a Triplex group with the Scenic Passenger Lifts with out any modifications being required. There will be a switch to control this located in the main security desk.
Lift Equipment Numbers All motor room equipment shall be marked with the lift number.
Interconnected Wiring Notice Provide on each controller.
Switch Functions Mark all motor room switches with permanent labels to indicate function.
Emergency Power N/A
Fire Alarm Required to shut the lifts down upon actuation of the Building Fire Alarm System, to auto return the lifts to the Ground floor allowing passengers to disembark and then to remain disabled with the doors closed.
Signal Feature linked to Provide
Fire Alarm panel
Car Entrances & Doors Centre opening automatic doors 1100mm wide x 2100m high clear openings.
Landing Entrances and Doors As above with small frame architraves, and with 2 hour certified fire rating.
Brushed stainless steel car and landing doors with slimline door frames in same finish.
Door Operator Type Variable Frequency Automatic operator. Medium usage.
Lift Car Finishes
- Half wall grey mirror mounted on upper half of rear wall.
- Side and rear walls fire treated hardwood veneer panels.
- Brushed finish stainless steel doors, brushed stainless steel finish to front wall and returns.
- Brushed finish stainless steel skirting 100mm high on each wall.
- Stainless steel tubular handrails to rear wall.
- fire treated hardwood veneer panels.
- Stone flooring (by others allow 50mm recess).
- Two-way voice communication for emergency communications at all times.
- Concealed ventilation at high and low level.
- Protective drapes – one set
- Drape stud fixings for protection during any goods usage - both lifts
Final finishes to be agreed. Costs to be included in the tender sum for a Mid range car finish
Lighting Concealed fluorescent lighting above ceiling panel, a minimum of 4 No 1500mm fluorescent lamps. Include for 3 hour non maintained emergency lighting.
Car Operating Panel Include within car side wall and suitable for disabled users in brushed stainless steel.
Car Door Protection Mechanical door protection plus full height infra red electronic door detector with high density beam pattern.
Car and Landing Sills Extruded Aluminium Section
(Include Full Width Landing Cill Support)
Top of Car Guard Rails Fit to the rear of each car.
Buffers Energy Dissipation
Full Fascias Include between the headers to sills.
Guide and Entrance Fixings Include for fixings to lift shaft steelwork by others.
Pit Ladder Provide and fix in pit.
Machine plinth ladder/rails N/A
Machine Guards Supply and fit.
Lift Supplies An 8 way single phase fuse board complete with RCD protected ways will be provided by others
Items indicated below to be connected to standard MCB’s on the above board.
§ Car lights
§ Shaft lights
§ Motor room heater
Items indicated below to be connected to RCD MCB’s of the above board.
§ Motor room socket outlet
§ Pit socket outlet
M/R Socket Included in the works for the Scenic lift
Shaft Lighting in each shaft Supply and install 1500mm vapour proof fluorescent fittings to provide 50 lux anywhere in the shaft including a fitting 500mm from the top and the bottom of the shaft complete with 2 way switching in the machine room and pit level. This circuit to be fed from the motor room fuse board.
Motor Room Lighting By others
Isolator Switch By others it will be a 3 phase and neutral Switch Fuse in the motor room – fuse size to be determined by CONTRACTOR - for each lift.
M/R Heating Included in the works for the Scenic lift
Emergency Lighting Provide one unit above each hoist unit.
Pit Stop Switch Include
Pit Socket Outlet Include to Pit. Twin metal clad socket fed from a RCD way on the above fuse board.
Intercom Unit N/A
Car Ventilation Centrifugal extract fan to the car roof controlled by a thermostat
Motor Room Ventilation By Others
Sound Isolation Machine/Car Include
Signals Car: Call Accepted Pushes
Alarm Push
Door Open Push
Car Preference Key Switch (Goods Control) – both lifts
L.C.D floor and direction indicator set above the car operating panel and clearly visible for any passenger within the lift car.
Landing: Call Accepted Pushes. Halo illumination.
Direction Indicators – at each floor level. Complete with Bi-Directional gongs.
Landing position indicator at every floor for each lift – L..C.D type
Note: All buttons to be tactile, illuminating micro movement in stainless steel.
All faceplates to be vandal proof screw fixings.
Voice Communication to lift car Include within the lift car for an automatic hands free auto-dial telephone system discretely mounted, with anti nuisance delay on alarm push.
Unit must have voice function and be fully compliant with EN81:1 1998 and GOST R Standards.
Manufacture to be third party type only
Telephone socket CONTRACTOR to connect to new auto-dialler.
Lifting Beam CONTRACTOR to provide
Lift Shaft Smoke Detector CONTRACTOR to provide
Shaft Smoke Vent CONTRACTOR to provide
Alarm System Alarm bell shall be fitted within the lift shaft at Ground Floor Level and also the provision of volt free contacts within the machine room, to be connected to a remote alarm system by CONTRACTOR.
Safety Gear Bi- Directional Safety Gear operated via a Bi-Directional overspeed governor.
Additional Items Audible floor Level Indicator system for emergency release.
Controller rubber mat.
Emergency stop switches adjacent to each gearbox..
All relevant notices, including:
Hand winding procedure.
Record Drawings Include.2 sets
Wiring Diagrams Include. One set of encapsulated Schematic wiring diagrams.
Operating & Maintenance Include.2 sets
Manuals
Maintenance Include for 12 monthly maintenance visits.
Callout coverage to be normal working hours